top of page
Concrete Wall

Structural Engineering Blog

Disclaimer: All articles and resources published in the  Pittsburgh Design & Engineering Services LLC, "PittDES" Structural Engineering Blog are provided for general educational purposes only. They do not constitute project-specific engineering advice, an assessment, design, report, or determination of structural safety or code compliance. Conditions and applicable requirements vary, and concealed conditions may exist. Reading this blog or contacting PittDES does not create an engineer-client relationship; professional services are provided only under an executed written agreement defining the applicable scope and limitations.

Anchor plate
Anchor plate

Many homeowners are advised to install wall anchors to repair bowing basement walls.

As a structural engineer who has evaluated thousands of homes across Pennsylvania and West Virginia, I’ve found that these repairs are sometimes recommended when they are not actually necessary.


In this article, we’ll explain what wall anchors actually do, when they are needed, and how homeowners can avoid paying for unnecessary foundation repairs.


Understanding Wall Anchors

Before we dive into the necessity of wall anchors, let's first understand what they are. Wall anchors are typically installed to stabilize foundation walls that have been pushed laterally into the basement space by external forces causing a bulge. They consist of the following components:

  • An interior steel plate installed on the basement wall: Typically a ribbed steel plate measuring approximately 11" × 18" or 12" × 28", along with a flat washer that distributes the load on the wall surface.

  • A threaded steel rod that passes through the wall: Threaded rod, typically 3/4" in diameter cold-rolled round bar, hot-dip galvanized with beveled washers and nuts on either side of the rod. 

  • Threaded coupler to allow splicing of the threaded rod.

  • An exterior anchor plate buried in the soil: Exterior soil anchor, typically made from 2 formed hot-dip galvanized steel plates.

  • Nuts and washers used to tighten the system. The system is installed by inserting the steel rod through the wall into the outside and running it to the appropriate distance where a hole is dug out, and the exterior soil anchor is attached to the rod. Calculations must be performed based on the geotechnical data to provide spacing of the anchors, how far the rod needs to run away from the wall, and how deep the plate for the reinforcement should be considered acceptable.

Anchor plate system
Anchor plate system
Anchor plate system installed
Anchor plate system installed

The Problem with Unnecessary Wall Anchors

Wall anchors can cost homeowners several thousand dollars.


But when they are installed unnecessarily, they can create additional problems including water entry through drilled holes and concerns during future home sales.


Water leaking behind washer of anchor plate
Water leaking behind washer of anchor plate

Misdiagnosed Cracks

One common reason for the unnecessary installation of wall anchors is misdiagnosed cracks. We have seen several instances where a foundation repair salesperson misdiagnosed the problem and sold the homeowner either an unnecessary product or the wrong solution.


Lack of Structural Significance

In many cases, minor movement of foundation walls does not pose a structural risk. Even if there is evidence of movement, it may not be necessary to intervene with wall anchors. The extent of movement and the absence of ongoing movement should be carefully evaluated by a licensed professional engineer before considering structural reinforcements.


The Cost of Unnecessary Wall Anchors

Aside from the potential lack of need for wall anchors, there are other factors to consider, such as the cost and the impact on the resale value of your home. Houses with visible wall anchors installed can be more difficult to sell, as buyers and, lately, some lenders may have reservations about them. It's essential to weigh the cost of installation against the actual need for wall anchors to avoid unnecessary expenses and potential complications in the future.


Signs That You May Need Wall Anchors

While it's important to be cautious about overselling wall anchors, there are situations where they may be necessary. Here are some signs that indicate you may need wall anchors for your foundation:


Visible Inward Displacement

If you notice visible inward displacement of your foundation walls, such as bowing or cracking, it's crucial to have a professional assessment. Significant displacement can compromise the structural integrity of your home and may require the installation of wall anchors or other approved products to stabilize the walls.


Ongoing Foundation Movement

If you observe ongoing movement or shifting of your foundation, it's essential to address the issue promptly by having an engineering assessment.


Professional Engineer Recommendation

When in doubt, it's always best to consult with a licensed Professional Engineer. They can assess the condition of your foundation and provide expert advice on whether any reinforcement type is necessary or if alternative solutions may be more suitable. Sometimes, alleviating the root cause may be sufficient to prevent further movement.


Before installing wall anchors, a licensed professional engineer should evaluate the foundation movement and determine whether structural reinforcement is actually required.



The Importance of Proper Installation

If wall anchors are deemed necessary for your foundation, it's crucial to ensure they are installed correctly. Unfortunately, many companies do not adhere to the requirements set forth by testing agencies, resulting in improper installations. Improperly installed wall anchors can be ineffective and may not provide the intended stability for your foundation.


To avoid such issues, it's recommended to choose a reputable company with a track record of proper installation and adherence to industry standards. Don't hesitate to ask for references and verify the qualifications and experience of the installation team. More importantly, always require the contracting firm to provide you with a stamped letter from a reputable, licensed, and local professional engineer approving the methods and certifying the installation.


Alternatives to Wall Anchors

In some cases, there may be alternative solutions to stabilize your foundation without the need for wall anchors. It's important to explore these options before committing to wall anchor installation. Here are a few alternatives to consider:


Carbon Fiber Straps

Carbon fiber straps can be an effective solution for stabilizing foundation walls. They are lightweight, extremely thin, durable, and can provide the necessary reinforcement without the need for extensive excavation, penetrating your wall with holes, or installing anchors. Carbon fiber straps are particularly useful for minor wall cracks and can be a cost-effective alternative to wall anchors.


Carbon Fiber Strap
Carbon Fiber Strap

Steel I-Beams/Tubes:

Installing Steel I-beams or other equivalent shapes such as tubes can be an alternative solution, so long reviewed, designed, and engineered also approved by the local municipality where you live.


Conclusion

Wall anchors can be an effective solution when they are truly needed and properly installed.

However, not every crack or minor wall movement requires structural reinforcement.

Before committing to an expensive repair, homeowners should consider having their foundation evaluated by a licensed structural engineer who can determine the true cause of the problem and recommend the most appropriate solution.


When Should You Contact a Structural Engineer?

If you notice:

• Bowing basement walls

• Horizontal cracking in block walls

• Walls leaning inward

• Signs of ongoing foundation movement


A structural evaluation can help determine whether reinforcement is necessary or if the issue can be addressed through less invasive solutions.



Written by Firas Abdelahad, P.E.

Firas Abdelahad has been a practicing structural engineer since 2005, collaborating with a diverse range of professionals, including consultants, architects, investors, homeowners, contractors, and subcontractors. Together, they tackle the various challenges that can arise during the design and construction phases of projects.

Firas has reviewed, evaluated, and assessed thousands of properties across the state of Pennsylvania, spanning from State College to Erie and throughout Western PA.


The information and statements in this document are for information purposes only and do not comprise the professional advice of the author or create a professional relationship between reader and author.

 
 
 

Updated: Sep 17, 2024


Improperly Supported jack post
Improperly Supported jack post


In the dynamic world of real estate, structural concerns often emerge after appraisals and inspections. Homeowners and real estate agents grapple with issues ranging from settlement concerns, sagging and improperly supported main load bearing beams, to compromised foundations. This blog discusses the critical role of structural engineering consulting in resolving these issues and emphasizes the potential pitfalls of opting for contractors over a structural engineer firm.

It highlights the importance of involving a structural engineering company to ensure the integrity of a property.


1. Early Intervention Saves Costs:


• Contacting a professional engineer early in the process can save homeowners, sellers, or buyers time and more importantly, significant costs. Engineering solutions ensure compliance with minimum code standards, satisfying both appraisals and mortgage requirements. While some concerns could be addressed in a structural inspection and maybe a letter, others may require structural repairs or intervention. Most municipalities require engineered stamped drawings for structural reinforcements.


2. Contractor vs. Structural Engineer Dilemma:


• While contractors play a crucial role, some contracting companies might mistakenly mislabel structural work as mere reinforcement, or just additional support when, in reality, it should have been a work that requires an engineering review, structural calculations, and drawings, followed by a contractor to pull the permit and perform the work. This misclassification becomes apparent during reevaluation that often is required by appraisers and loan officers, leading to additional costs and potential complications.


3. The Aftermath of Misjudgment:


• Clients opting for contractors often face post-installation appraisals that demand structural engineer approval. This step becomes problematic when the initial work fails to meet code standards, necessitating costly corrections. It also gets expensive as the registered professional engineer or licensed professional will need to verify whether the work completed meets the load requirements or if it needs adjustment and modifications.


4. The Engineering work:


• Structural engineering involves load calculations, correct beam spans, proper footing size, and appropriate load path distribution. Failure to adhere to these principles can result in non compliance work.

Conclusion:


In navigating the complexities of real estate transactions, our advice to real estate agents, sellers, and buyers in Pennsylvania is clear: involve a structural engineer early on. By doing so, you can mitigate potential problems, save time, and reduce costs. Appraisals should also prioritize evaluations by a Pennsylvania structural engineer before greenlighting any structural work. This proactive approach ensures that any structural modification done is sound and meets the minimum requirements set by the structural engineering standards for Pennsylvania.



Written by Firas Abdelahad, P.E.

Firas Abdelahad has been a practicing structural engineer since 2005, collaborating with a diverse range of professionals, including consultants, architects, investors, homeowners, contractors, and subcontractors. Together, they tackle the various challenges that can arise during the design and construction phases of projects.

Firas has reviewed, evaluated, and assessed thousands of properties across the state of Pennsylvania, spanning from State College to Erie and throughout Western PA.


The information and statements in this document are for information purposes only and do not comprise the professional advice of the author or create a professional relationship between reader and author.

 
 
 

Updated: 3 days ago

Push pier installation, an actual job in Pittsburgh
Push pier installation

Introduction:

A building’s foundation transfers structural loads to the supporting soil or rock. Cracking, bowing, displacement, settlement, moisture exposure, material deterioration, or previous alterations may affect how a foundation performs.

These conditions do not necessarily establish that a foundation has failed or that reinforcement is required. Their significance depends on factors such as the foundation type, construction materials, soil and drainage conditions, loading, observed movement, available construction information, and the condition of the surrounding structure.

A structural engineering evaluation can help document accessible conditions, identify relevant structural considerations, and determine whether additional investigation, monitoring, maintenance, repair design, or reinforcement may be appropriate.


Why Foundation Evaluation Comes First

Foundation reinforcement should be selected only after the condition and reasonably apparent contributing factors have been evaluated. Similar visible symptoms can result from different causes and may not require the same response.

For example, foundation cracking or movement may be associated with soil settlement, lateral earth pressure, inadequate drainage, moisture changes, deterioration, insufficient reinforcement, altered loading, nearby construction, or a combination of conditions. A repair system intended for one cause may not adequately address another.

The evaluation may include reviewing available documents and history, observing accessible conditions, taking measurements, documenting crack patterns or displacement, and considering whether additional information is needed. Depending on the circumstances, that additional information may include monitoring, exploratory openings, material testing, subsurface investigation, drainage evaluation, or consultation with a geotechnical professional.


Conditions That May Warrant Evaluation:

Conditions that may warrant a structural engineering evaluation include:

  • Foundation walls that appear bowed, leaning, displaced, or separated

  • Cracks accompanied by measurable displacement or continuing movement

  • Stair-step cracking in masonry walls

  • Changes in floor elevation or localized floor movement

  • Separation between walls, framing, floors, or other connected elements

  • Doors or windows that have recently become difficult to operate

  • Deterioration, spalling, corrosion, or moisture-related damage

  • Previous reinforcement or repair work of uncertain design or installation

  • Drainage, grading, or water conditions that may be affecting the foundation

  • Proposed alterations that may change the loads carried by the foundation

No single symptom determines whether a foundation is structurally deficient. The location, orientation, extent, displacement, history, rate of change, and relationship to surrounding construction should be considered together.


Selecting a Structural Engineer for a Foundation Evaluation:

When selecting an engineer, confirm that the individual is properly licensed for the jurisdiction and has experience relevant to the foundation type and reported conditions.

Before authorizing the work, ask the engineer to identify:

  • The conditions or questions included in the evaluation

  • Whether the service includes a site visit, measurements, document review, calculations, monitoring, or testing

  • Whether the initial service is verbal consultation or includes written documentation

  • Whether repair design or signed and sealed drawings are included

  • What conditions or areas will not be accessible or included

  • Whether another discipline, such as geotechnical engineering, geology, surveying, or materials testing, may be needed

A clearly defined scope helps establish what the engineer will evaluate and what deliverables will be provided.


Potential Foundation Repair and Reinforcement Approaches:

The appropriate repair or reinforcement depends on the foundation system, observed conditions, contributing factors, loads, site constraints, and available supporting information. Potential approaches may include:

Wall Reinforcement

Steel members, reinforced concrete elements, engineered composite systems, or other structural components may be used in appropriate applications to resist lateral loads or stabilize an existing foundation wall. The suitability of any system depends on the wall material, geometry, condition, displacement, connections, and required load path.


Underpinning or Supplemental Support

Underpinning systems may be considered when additional foundation support is required. Potential systems include conventional reinforced concrete underpinning, helical piles, resistance piers, micropiles, or other project-specific solutions. Selection generally requires consideration of structural loads, soil conditions, access, installation

effects, and the condition of the existing foundation.


Localized Repair or Partial Replacement

Localized deterioration or damage may sometimes be addressed through repair, reconstruction, or partial replacement. The extent of work should be based on the condition of the remaining material and the ability of the repaired system to transfer the applicable loads.


Drainage and Moisture Management

Correcting grading, downspout discharge, surface drainage, plumbing leakage, or other moisture sources may be an important part of addressing conditions affecting a foundation. Drainage work does not, by itself, establish that existing structural displacement or damage has been corrected.


Monitoring or Further Investigation

When the extent or progression of movement is uncertain, monitoring or additional investigation may be appropriate before selecting a permanent structural repair. Monitoring should have a defined purpose, method, duration, and evaluation criteria.

A commercially available repair product should not be selected solely because it is commonly used or readily available. Its applicability should be evaluated for the actual conditions and intended structural function.


Engineering and Construction Responsibilities:

When repair design is required, the engineer may prepare calculations and signed and sealed drawings identifying the structural components and details included in the agreed scope. The contractor remains responsible for construction means, methods, sequencing, temporary protection, temporary shoring, site safety, and installation in accordance with the applicable construction documents and manufacturer requirements.

If concealed conditions differ from the information used for the design, work in the affected area should pause until the condition can be evaluated. Field changes to structural components should be reviewed by the responsible design professional before implementation.

Depending on the project, construction observations may be recommended to evaluate whether visible portions of the work appear generally consistent with the engineering documents. Such observations are not continuous inspections and do not make the engineer responsible for the contractor’s workmanship or construction procedures unless specifically stated in the agreement.


Foundation Evaluations in Pittsburgh and Western Pennsylvania:

Foundation conditions should be evaluated based on the specific property, construction, accessible evidence, and agreed scope of services. Cracking or movement does not automatically require extensive reinforcement, but visible conditions should not be dismissed without appropriate consideration.

Pittsburgh Design & Engineering Services provides independent structural evaluations of accessible foundation and basement-wall conditions. Depending on the findings and separately authorized scope, additional services may include measurements, written engineering opinions, structural calculations, or signed and sealed repair drawings.

PittDES does not sell or install foundation-repair or waterproofing systems. Recommendations are developed from the observed conditions, available information, applicable engineering requirements, and the limitations of the agreed evaluation.


Call us today if you need any further assistance: 724-949-0004



Written by Firas Abdelahad, P.E.

Firas Abdelahad has been a practicing structural engineer since 2005, collaborating with a diverse range of professionals, including consultants, architects, investors, homeowners, contractors, and subcontractors. Together, they tackle the various challenges that can arise during the design and construction phases of projects.


This article provides general educational information and is not a project-specific engineering opinion, repair design, or substitute for an evaluation of the actual property. Foundation and soil conditions vary, and concealed conditions may differ from those visible during a limited evaluation. Reading this article does not create an engineer-client relationship with Pittsburgh Design & Engineering Services LLC.

 
 
 
bottom of page